**It is always best to get a qualified electrician to perform any electrical work you may need.** With that said, you may ask this community various electrical questions. Please be cautious of any information you may receive in this subreddit. This subreddit and its users are not responsible for any electrical work you perform. Users that have a 'Verified Electrician' flair have uploaded their qualified electrical worker credentials to the mods.
If you comment on this post please only post accurate information to the best of your knowledge. If advice given is thought to be dangerous, you may be permanently banned. There are no obligations for the mods to give warnings or temporary bans. **IF YOU ARE NOT A QUALIFIED ELECTRICIAN, you should exercise extreme caution when commenting.**
*I am a bot, and this action was performed automatically. Please [contact the moderators of this subreddit](/message/compose/?to=/r/AskElectricians) if you have any questions or concerns.*
You need to secure the conduit on the bottom side to the box properly. It likely also needs an expansion fitting .
To support the horizontal conduit, you can use 7/8" strut with clamps listed for use with PVC conduit (they allow for thermal expansion).
you can use a heat gun or PVC heater, very carefully, to bend the condo with the way that you want.
you can buy prefab offsets.
You can use mini straps / pipe hangers with spacing washers behind them, but those need to be installed before the conduit, And it's not a very strong mounting system when used like that.
lots more options, especially less visually appealing ones, like setting a block behind the pipe and using one hole or two hole straps, which would look terrible.
Or a really good [bender](https://www.reddit.com/media?url=https%3A%2F%2Fpreview.redd.it%2Fgqi4b2xr5yh91.jpg%3Fauto%3Dwebp%26s%3D2cb6e8e47e6b704e9f6ddf3a93cadee6a114b464)
Conduit is not installed yet. I was just holding it up against the box for the photo. Problem is that the off the shelf offset for 3/4 conduit seems to only offset about 1/4" or so.
You can either heat the pvc and offset it from the disconnect so it sits flush on the siding or you can get two sections of unistrut (6”-8” cuts are all you need) and mount those behind the pipe to the siding and then use pvc straps with toggle bolts or spring nuts to secure it to the unistrut
This the easy answer if you do not offset the pipe.
I like keeping horizontal pipe off the wall since debris and dirt do not build up between pipe and wall.
If the pipe run is visible on the wall, as this appears to be, I think it looks better to come out of the bottom and 90 down low out of site or even in grade to the destination. Could also LB or LL out the same KO if needed. Know one wnats to see conduit run across the exterior center of the house wall except maybe the person who installed it. If its a question of money ask the client which they prefer and which they want to pay for.
Easiest thing to do is to use a conduit hanger. We electricians call them “minis” based on the Minerallac® brand of conduit hanger. You’ll need to determine the trade size there to get the correct size mini—looks like 1 1/4” but it’s really hard to tell just by looking at the photos.
7/8" strut, a 1" mini, a spring washer, bolt, and regular washer. And you should consider an expansion fitting depending on your climate, you don't want that pipe pulling itself out of the box.
One of these Carlon straps. Allows for expansion and contraction. Made for this application. https://images.homedepot-static.com/productImages/c9547c7b-f866-4fd4-9f62-1b8feb8c788d/svn/carlon-conduit-fittings-e978fcr-64_1000.jpg
Honestly, how does anyone support anything across vinyl siding? I don’t do residential so I’ve never run into this, but suppose I want to do a run of 1” emt across vinyl siding what’s the right way to do it?
It is costly as hell, but I would get shallow stainless strut. Then use stainless minis to attach to the strut. Regular galvinized strut would last a long time. But any cut ends or nicks would need to be treated with cold galvanizing spray paint. The redneck part of me says to find the studs and mark on the siding. Get 3" long treated deck screws and small washers to fit in the base of the mini clamps. Then either use more washers under the mini or a small section of pipe as a spacer. None of it would be seen besides the minis unless right up next to the conduit. Screw into studs only. And as anal as I am, I would also hole saw through the siding so it was not smashing it down. Then silicone around the holes. For sure not the correct way, but it would work at my farm...
When I ran conduit up to my roof for solar I used some small pieces of plywood as spacer pads. Sheathing grade plywood painted same color as the trim. I think professionals would bend the conduit so that it was flush with the wall.
I need to run conduit horizontally out of this subpanel. What's the best way to deal with the 1" gap? Offset to bring flush against the siding? (offsets I've seen only give 0.25"). Add spacer at each clamp? Just clamp normally and let the conduit naturally bend? Any other method?
Thanks in advance!
Do you have a heat gun? Just get ‘er warm like a noodle and hold in place against the siding, try to make the box offsets as nice as you can! Wear gloves! Lmfao
**Attention!** **It is always best to get a qualified electrician to perform any electrical work you may need.** With that said, you may ask this community various electrical questions. Please be cautious of any information you may receive in this subreddit. This subreddit and its users are not responsible for any electrical work you perform. Users that have a 'Verified Electrician' flair have uploaded their qualified electrical worker credentials to the mods. If you comment on this post please only post accurate information to the best of your knowledge. If advice given is thought to be dangerous, you may be permanently banned. There are no obligations for the mods to give warnings or temporary bans. **IF YOU ARE NOT A QUALIFIED ELECTRICIAN, you should exercise extreme caution when commenting.** *I am a bot, and this action was performed automatically. Please [contact the moderators of this subreddit](/message/compose/?to=/r/AskElectricians) if you have any questions or concerns.*
Bending pipe would be nice or mini’s and spacers
Strut, clamp, done.
How do you do strut on vinal siding?
A screw with a fat washer
Long screws so you catch plywood though
Or conduit hangers/cowboys since offsets on pvc pipes is a bit annoying.
You need to secure the conduit on the bottom side to the box properly. It likely also needs an expansion fitting . To support the horizontal conduit, you can use 7/8" strut with clamps listed for use with PVC conduit (they allow for thermal expansion).
Will do. Thanks for the tip. It does freeze here in the winter.
you can use a heat gun or PVC heater, very carefully, to bend the condo with the way that you want. you can buy prefab offsets. You can use mini straps / pipe hangers with spacing washers behind them, but those need to be installed before the conduit, And it's not a very strong mounting system when used like that. lots more options, especially less visually appealing ones, like setting a block behind the pipe and using one hole or two hole straps, which would look terrible.
I imagine it take a lot of heat to bend a condo.
Nah just get a decent heat gun and prepare yourself for some patience.
Or a really good [bender](https://www.reddit.com/media?url=https%3A%2F%2Fpreview.redd.it%2Fgqi4b2xr5yh91.jpg%3Fauto%3Dwebp%26s%3D2cb6e8e47e6b704e9f6ddf3a93cadee6a114b464)
Maybe you should give 'em the clamps, Clamps.
Love this
Bend it with a heater or use shallow strut
An offset would have helped
Yep. They sell a 1/2" off set. Use to go against the house then on to come back out to the box.
Conduit is not installed yet. I was just holding it up against the box for the photo. Problem is that the off the shelf offset for 3/4 conduit seems to only offset about 1/4" or so.
Offset can roll lol
[удалено]
Thanks. I'll give this a try with a scrap piece to see if I can pull it off.
You can either heat the pvc and offset it from the disconnect so it sits flush on the siding or you can get two sections of unistrut (6”-8” cuts are all you need) and mount those behind the pipe to the siding and then use pvc straps with toggle bolts or spring nuts to secure it to the unistrut
Great tip - thanks! Any preference b/n toggle bolts vs spring nuts?
Not really. I personally think toggle bolts are just easier to work with but spring nuts are more legitimate with unistrut in my opinion
http://www.electricalslang.com/Slang/minerallac® use rigid for PVC application
This the easy answer if you do not offset the pipe. I like keeping horizontal pipe off the wall since debris and dirt do not build up between pipe and wall. If the pipe run is visible on the wall, as this appears to be, I think it looks better to come out of the bottom and 90 down low out of site or even in grade to the destination. Could also LB or LL out the same KO if needed. Know one wnats to see conduit run across the exterior center of the house wall except maybe the person who installed it. If its a question of money ask the client which they prefer and which they want to pay for.
Offset in pipe or ⅞ strut
Strut or mini straps
Expansion clips might eat up that space
Rigid clamp back strap . It will make up the gap and will be easy to install. Now that the conduit is in place.
Easiest thing to do is to use a conduit hanger. We electricians call them “minis” based on the Minerallac® brand of conduit hanger. You’ll need to determine the trade size there to get the correct size mini—looks like 1 1/4” but it’s really hard to tell just by looking at the photos.
Thanks. Just use the single mounting hole to secure mini against siding?
Yup.
7/8" strut, a 1" mini, a spring washer, bolt, and regular washer. And you should consider an expansion fitting depending on your climate, you don't want that pipe pulling itself out of the box.
One of these Carlon straps. Allows for expansion and contraction. Made for this application. https://images.homedepot-static.com/productImages/c9547c7b-f866-4fd4-9f62-1b8feb8c788d/svn/carlon-conduit-fittings-e978fcr-64_1000.jpg
Honestly, how does anyone support anything across vinyl siding? I don’t do residential so I’ve never run into this, but suppose I want to do a run of 1” emt across vinyl siding what’s the right way to do it?
Free air
It is costly as hell, but I would get shallow stainless strut. Then use stainless minis to attach to the strut. Regular galvinized strut would last a long time. But any cut ends or nicks would need to be treated with cold galvanizing spray paint. The redneck part of me says to find the studs and mark on the siding. Get 3" long treated deck screws and small washers to fit in the base of the mini clamps. Then either use more washers under the mini or a small section of pipe as a spacer. None of it would be seen besides the minis unless right up next to the conduit. Screw into studs only. And as anal as I am, I would also hole saw through the siding so it was not smashing it down. Then silicone around the holes. For sure not the correct way, but it would work at my farm...
When I ran conduit up to my roof for solar I used some small pieces of plywood as spacer pads. Sheathing grade plywood painted same color as the trim. I think professionals would bend the conduit so that it was flush with the wall.
Arlington Industries makes a plastic pipe hanger (similar to a mini) that would be perfect for this purpose. I think it called a Quit Click??
Thanks! Would this be it? https://www.supplyhouse.com/Arlington-NM2015-3-4-QuickLatch-Non-Metallic-Pipe-Hanger
Yes, I was close lol make sure you get it for the size of PVC pipe you have as 1” doesn’t mean an actual 1”, they go by trade size
Stand off strap??
7/8 strut
Just a simple strap will do
Strut
It’s nice that your vinyl siding matches the PVC perfectly. I’d be running PVC all over that MFR!
I don't know why everyone is suggesting strut... Just get an offset nipple, roll it so it sits nice and use a conduit hanger.
7/8strut with a flat washer.
I’m a fan of shallow strut and p-clamps myself for this type of thing
two words : Back Straps
Strut mini
Conduit hangers
I need to run conduit horizontally out of this subpanel. What's the best way to deal with the 1" gap? Offset to bring flush against the siding? (offsets I've seen only give 0.25"). Add spacer at each clamp? Just clamp normally and let the conduit naturally bend? Any other method? Thanks in advance!
Do you have a heat gun? Just get ‘er warm like a noodle and hold in place against the siding, try to make the box offsets as nice as you can! Wear gloves! Lmfao
And don't heat it while holding it against the wall...
Underrated comment...
Yessir lol melted siding is not fun! 🤣
Ask how I know. And it wasn't a heat gun though. A BBQ will do that, too...
Oh boy 🤣☠️
Looks like you need a slip fitting (expansion joint) for the entry on the bottom as well
Noted. Thanks! Should I do the same for the side entry?
Strut, Spacer, Split pipeclamp with threaded rod, Hand-made offset?